That is new section in 2011 NEC.
If they have not gotten used to installers asking about it then you have just recently adopted the 2011, or the inspectors have not been enforcing that new section.
I get funny looks from them sometimes myself, and generally just find out what size their transformer is and the impedance and do calculations myself. This will not necessarily give accurate results, but instead a worst case result. If your equipment can handle worst case then it should be safe. When you get results that are close to max equipment ratings you must then either get higher rated equipment or get more serious about accuracy.
Most basic calculations assume infinite transformer supply capabilities when in reality there is limits to the supply, (distance and size of conductors to substation, and the impedance of the sub as well as the incoming supply to the sub are also factors) so most instances the calculation results in worst case scenario assuming infinite supply at the transformer supply terminals.