110.26(6)

NTesla76

Senior Member
Location
IA
Occupation
Electrics
110.26(6) is new for 2023. Grade, Floor, or working platform has to be 'level and flat as practical'. As an AHJ, this interpretation seems like it is up to me. If I had an outdoor panel or equipment, and it has a steep grade away from the building for the working space, how far does one take it to make the space 'level an flat as practical'? Iowa is still dragging along on the 2020 NEC. I'm curious as to how others are accomplishing this requirement.
 
I find the level ground thing to be silly. Unless this is on the side of a cliff if someone were able to work on the equipment when they actually installed in on the slope then someone can work on it after it's installed.
 
I find the level ground thing to be silly. Unless this is on the side of a cliff if someone were able to work on the equipment when they actually installed in on the slope then someone can work on it after it's installed.
Those were my thoughts when I first read about this new requirement.
 
Those were my thoughts when I first read about this new requirement.
Unless the NEC is going to give you a measurable amount of acceptable slope these requirements border on meaningless because how can you enforce them?

Ambiguity is the enemy of code language although the NEC doesn't seem to have a problem with it lately.
 
I'd have a hard time telling someone to get the landscape blocks ready to level an area out. Then building codes would come into play with rise/run, handrails and guards, etc......:rolleyes:
 
110.26(6) is new for 2023. Grade, Floor, or working platform has to be 'level and flat as practical'. As an AHJ, this interpretation seems like it is up to me. If I had an outdoor panel or equipment, and it has a steep grade away from the building for the working space, how far does one take it to make the space 'level an flat as practical'? Iowa is still dragging along on the 2020 NEC. I'm curious as to how others are accomplishing this requirement.
I would lean to sizing for the table 110.26(A)(1) rules. But with a slope away a little less of a safety issue than a lateral slope or worse a slope toward the panel where a small off balance can put you into the panel rather than away. AHJ has some discretion on the interpretation of this. With a slope away or lateral you could build a platform in front of the panel to the size requirements of the working space.
 
Unless the NEC is going to give you a measurable amount of acceptable slope these requirements border on meaningless because how can you enforce them?

Ambiguity is the enemy of code language although the NEC doesn't seem to have a problem with it lately.
Probably got a few wood or concrete manufacturers on the CMPs nowadays.
 
Isn't there a code rule about mounting a panel over a set of stairs regardless how wide and steep they are?
Another stupid rule IMO. Stairs are a great spot for panels actually, people can't put crap in front of them or build cabinets over them - oh yeah, CMP's wouldn't know that they are so out of touch and clueless. Seems like there isn't a single actual electrician on them.