I have a situation where there is a 480V Automatic Transfer Switch and as you would be working on the ATS behind you would be the side of a 1600A 480V Main Distribution Panel.
I am thinking that first of all this would be a Condition 2 in Table 110.26(A)(1) requiring 3.5' of clearance.
Secondly that according to the last sentence of 110.26(A)(1) that the distance of 3.5' would be measured from the front of the enclosure for the ATS and not from the circuit breaker/Bussing inside the ATS.
Let me know your thoughts on this if I am thinking of this correctly.
Thanks,
Ed
I am thinking that first of all this would be a Condition 2 in Table 110.26(A)(1) requiring 3.5' of clearance.
Secondly that according to the last sentence of 110.26(A)(1) that the distance of 3.5' would be measured from the front of the enclosure for the ATS and not from the circuit breaker/Bussing inside the ATS.
Let me know your thoughts on this if I am thinking of this correctly.
Thanks,
Ed