southman
Member
- Location
- jacksonville, fl
Transformer with 277/480V secondary has meter can mounted on side. An ATS is being installed on side of transformer with the meter. My thought is the ATS, being grounded, represents condition 2 and requires 42" minimum working space between it and the meter. Understand the actual meter can stick into the working space 6". Is there anyway this would be a condition 1?
Last edited: