110.26 (A)(1) working space

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have a 480V panel installed 30” from an access gate. Construction is saying it’s ok since the gate is interlocked with the panel. So it won’t be worked on while energized - I believe this is compliant “as is”
Thoughts


Sent from my iPhone using Tapatalk
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Maybe you’re ok then if gate wider than panel and can be opened quickly to allow access to panel.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
If the gate is wider than the panel, the opening allows working space, it would be no different than an electrical panel with a door in a hallway that opens in front of the panel
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There are two requirements, one is for the working space and two it needs to be readily accessible. So if the panel is readily accessible with the gate closed and the gate can be opened to provide the required working space then it's code compliant.
 