110.26(A)

Pinnie

Humble Disciple
Location
Ohio
Occupation
Commercial Electrician
“ working space for equipment, operating at 1000 V nominal or less to ground and likely to require examination, adjustment, servicing or maintenance while energized…”

What would and wouldn’t fit this category in your opinions?
 
What wouldn't fit is something that you would absolutely not examine while energized which isn't much. Equipment is so broad that it can apply to almost anything electrical.
 
What wouldn't fit is something that you would absolutely not examine while energized which isn't much. Equipment is so broad that it can apply to almost anything electrical.
I was gonna say nothing really comes to mind. Even a receptacle could need examining.
 
I agree. That section is so poorly written that it needs to be fixed or removed from the NEC.
110.26(b) “Low Voltage. Special permissions, smaller, working spaces shall be permitted were all exposed live parts operate at not greater than 30 V RMS, 42 V peak, or 60 V DC.“

I’m not seeing the smaller dimensions allowed am I blind?
 
110.26(b) “Low Voltage. Special permissions, smaller, working spaces shall be permitted were all exposed live parts operate at not greater than 30 V RMS, 42 V peak, or 60 V DC.“

I’m not seeing the smaller dimensions allowed am I blind?

Is that because only smaller people work on low voltage? lol
 
110.26(b) “Low Voltage. Special permissions, smaller, working spaces shall be permitted were all exposed live parts operate at not greater than 30 V RMS, 42 V peak, or 60 V DC.“

I’m not seeing the smaller dimensions allowed am I blind?
Those are decided by your AHJ when he provides the written special permission.
 