Long time reader (4.5 years), first time poster. If this is in the wrong spot, please feel free to move.
Curious of other's interpretation of 110.26(C)(3). Would this apply if an 800A rated MDP is used with a 600A MCB?
110.26(C)(3) reads: Where equipment rated for 800 amperes or more that contains overcurrent devices, switching devices, or control devices is installed and there is a personnel door(s) intended for entrance to or egress from the working space less than 7.6m (25ft) from the nearest edge of the working space, the door(s) shall open in the direction of egress and be equipped with listed panic hardware or listed fire exist hardware.
My thought would be yes based on text above. I have 800A rated equipment with overcurrent protective devices in it which would require the listed panic hardware. On the other hand, the max capacity of the service conductors and main breaker are only rated for 600A so there is not 800A available.
Curious of other's interpretation of 110.26(C)(3). Would this apply if an 800A rated MDP is used with a 600A MCB?
110.26(C)(3) reads: Where equipment rated for 800 amperes or more that contains overcurrent devices, switching devices, or control devices is installed and there is a personnel door(s) intended for entrance to or egress from the working space less than 7.6m (25ft) from the nearest edge of the working space, the door(s) shall open in the direction of egress and be equipped with listed panic hardware or listed fire exist hardware.
My thought would be yes based on text above. I have 800A rated equipment with overcurrent protective devices in it which would require the listed panic hardware. On the other hand, the max capacity of the service conductors and main breaker are only rated for 600A so there is not 800A available.