I have a question regarding the layout of electrical closets according to Article 110.26(C) Entrance to and Egress From Workspace.
I have a 208V, 3ph, 4w 2500A main service switch board. it is over 6 feet long and it is L shaped. I understand the requirements of 110.26(C)(2)(a)&(b) however....
I would like to install one door in my electrical closet. I can maintain double workspace (6ft) in front of all my equipment and I can located the door more than 3 feet away from my 1200A, 6foot switchboard.
Now the question....
Do the requirements of 110.26(C)(2)(b) require even a 100A panel to be located 3ft away from the egress door as well?
I interpret the code to mean the requirements of 110.26(C)(2) only apply to the Large Equipment and not smaller equipment located in the electrical closet.
Attached I have located a panel within 3ft of the door to illustrate my point.