Rick Christopherson
Senior Member
I had a customer ask a question and I'm not sure whether the NEC 110.26 applies or not. This is a manufactured (skid mounted) piece of equipment with PLC and VFD control panels. Do the clearances of 110.26 apply to this type of equipment/installation? Here are some details:
- It's skid mounted, but not portable as it is hard plumbed and hard wired.
- It is served by a typical 20-amp, 3-phase circuit (208 to 480), connected to an on-board door-lockout handle and internal overload protection.
- Due to the door lockout, only the incoming power terminals can be energized if the control panel door is opened.
- Except for external sensors, everything is pre-fabricated and self contained.