I've got an electrical room with 480V gear. It falls under the category of Large Equipment. I've got panelboards on the opposite side of the room, so my Table 110.26(A)(1) Working Space is Condition 3, or 4'. The depth of the working space is twice what is required by Table 110.26(A)(1).
What is my required distance to the entrance (door)? See attached PDF. Per 110.26(C)(2), "a single entrance shall be permitted...located such that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition."
It seems like "that condition" would refer to the condition of the gear with respect to the entrance, which would be Condition 2 (3.5'), not the condition of the room as a whole, or Condition 3 (4').
Does this interpretation gibe with others experience?
What is my required distance to the entrance (door)? See attached PDF. Per 110.26(C)(2), "a single entrance shall be permitted...located such that the distance from the equipment to the nearest edge of the entrance is not less than the minimum clear distance specified in Table 110.26(A)(1) for equipment operating at that voltage and in that condition."
It seems like "that condition" would refer to the condition of the gear with respect to the entrance, which would be Condition 2 (3.5'), not the condition of the room as a whole, or Condition 3 (4').
Does this interpretation gibe with others experience?