jwelectric
Senior Member
- Location
- North Carolina
1- Section/Paragraph
110.26 Spaces About Electrical Equipment.
(D) Illumination. Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, or motor control centers installed indoors. Additional lighting outlets shall not be required where the work space is illuminated by an adjacent light source or as permitted by 210.70(A)(1), Exception No. 1, for switched receptacles. In electrical equipment rooms, the illumination shall not be controlled by automatic means only.
210.70 (A) (1) Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
2- Proposal Recommends New Text
3- Proposal
110.26 Spaces About Electrical Equipment.
(D) Illumination. Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, or motor control centers installed indoors. Additional lighting outlets shall not be required where the work space is illuminated by an adjacent light source or as permitted by 210.70(A)(1), Exception No. 1 and 410.30 (C) for cord and plug connected fixtures . In electrical equipment rooms, the illumination shall not be controlled by automatic means only.
4- Statement of Problem and Substantiation for Proposal
NEC Manual of Style states: 2.6 Exceptions. 2.6.1 Placement and Order. Exceptions shall immediately follow the main rule to which they apply. Where exceptions are made to items within a numbered list, the exception shall clearly indicate the items within the list to which it applies.
As written this article could and sometimes is interpreted as not allowing a cord and plug fixture in a warehouse or industrial setting around panels and motor controllers.
The NEC is clear in 410.30 that a fixture can be cord and plug connected. The problem arises when a cord and plug fixture is being switched at a panel in a warehouse or industrial setting. This seems to be noncompliant by 110.26 referring to the exception in 210.70 (A) (1), Exception 1 as this refers to a habitable room in a dwelling unit
edited to show bold in #3 those words to be underlined
[ March 01, 2005, 10:46 PM: Message edited by: jwelectric ]
110.26 Spaces About Electrical Equipment.
(D) Illumination. Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, or motor control centers installed indoors. Additional lighting outlets shall not be required where the work space is illuminated by an adjacent light source or as permitted by 210.70(A)(1), Exception No. 1, for switched receptacles. In electrical equipment rooms, the illumination shall not be controlled by automatic means only.
210.70 (A) (1) Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
2- Proposal Recommends New Text
3- Proposal
110.26 Spaces About Electrical Equipment.
(D) Illumination. Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, or motor control centers installed indoors. Additional lighting outlets shall not be required where the work space is illuminated by an adjacent light source or as permitted by 210.70(A)(1), Exception No. 1 and 410.30 (C) for cord and plug connected fixtures . In electrical equipment rooms, the illumination shall not be controlled by automatic means only.
4- Statement of Problem and Substantiation for Proposal
NEC Manual of Style states: 2.6 Exceptions. 2.6.1 Placement and Order. Exceptions shall immediately follow the main rule to which they apply. Where exceptions are made to items within a numbered list, the exception shall clearly indicate the items within the list to which it applies.
As written this article could and sometimes is interpreted as not allowing a cord and plug fixture in a warehouse or industrial setting around panels and motor controllers.
The NEC is clear in 410.30 that a fixture can be cord and plug connected. The problem arises when a cord and plug fixture is being switched at a panel in a warehouse or industrial setting. This seems to be noncompliant by 110.26 referring to the exception in 210.70 (A) (1), Exception 1 as this refers to a habitable room in a dwelling unit
edited to show bold in #3 those words to be underlined
[ March 01, 2005, 10:46 PM: Message edited by: jwelectric ]