I am currently designing an enclosed pump/filter skid module
I have a pretty tight space with a control panel that encloses (3) 480V VFD's. The front of the panel has some 120V indicator lights on it and 120V selector switches.
The panel is 18" deep and I have a clearance of about 40" from the front of the panel.
When the panel is opened, I have about 44" clearance from the front of the 480V VFD's.
110.26 (A)(1) says distances shall be measured from the enclosure or opening if live parts are enclosed.
Does this mean I need 42" front he front of the enclosure too? I am not sure if I meet Condition 1 of the accompanying table. The live parts are not really on the front of the plastic VFD enclosure but in the back.