Is this a violation of dedicated space or even work clearance?
Sent from my iPhone using Tapatalk
Forty extension cords - even worse.![]()
It is inside a cabinet and tecnically the panels on bottom and top of cabinet violate the clearance I think
Sent from my iPhone using Tapatalk
There is nothing about this that complies with Art 590.They only use them for a month so it complies with the temporary wiring but I will say it was not the best plan.
There is nothing about this that complies with Art 590.
590.3 Time Constraints
590.3.A During Period of Construction - Nope , no construction
590.3.B 90 Days - only applies to holiday decorative lighting, so Nope
590.3.C Emergencies and Tests - Ahh, Nope
I'm not saying it is wrong. I'm saying it has nothing to do with temporary power.