1- Section/Paragraph
110.26(E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6? ft).
2- Proposal Recommends New Text
3- Proposal
(E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
Exception: In existing dwelling units, existing or replacement service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6? ft).
4- Statement of Problem and Substantiation for Proposal
As written 110.26 (E) exception could and has been thought to mean that any existing dwelling no matter how old or new could have a service change and the new panel not have to comply to the six foot six inch rule as outlined in 110.26 (E)
As worded a new house the day after receiving a Certificate of Occupancy could have the service panel moved to a place such as a crawl space or under a deck.
There needs to be a more concise meaning as to the intent of the exception.
[ March 07, 2005, 06:14 PM: Message edited by: dccc_man ]
110.26(E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6? ft).
2- Proposal Recommends New Text
3- Proposal
(E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
Exception: In existing dwelling units, existing or replacement service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6? ft).
4- Statement of Problem and Substantiation for Proposal
As written 110.26 (E) exception could and has been thought to mean that any existing dwelling no matter how old or new could have a service change and the new panel not have to comply to the six foot six inch rule as outlined in 110.26 (E)
As worded a new house the day after receiving a Certificate of Occupancy could have the service panel moved to a place such as a crawl space or under a deck.
There needs to be a more concise meaning as to the intent of the exception.
[ March 07, 2005, 06:14 PM: Message edited by: dccc_man ]