Can an electrical item be considered ?foreign? to an electrical installation?
Situation: Three transformers are in a vault that is next to the main electrical room. Bus duct will be used to connect three network protectors to the main switchboard?s main breaker. Space is limited. At the moment, I am showing an ATS and a Distribution Panel on the electrical room wall, and the path of the bus duct goes right over them.
Is this a violation of 110.26(F)(1)(a)? The last sentence of that paragraph says, ?. . . no OTHER (my emphasis) equipment foreign to the electrical installation shall be located in this space.? When you are talking about the Distribution Panel, would the bus duct be considered ?foreign? to its installation? Am I going to have to shuffle some things around?
Situation: Three transformers are in a vault that is next to the main electrical room. Bus duct will be used to connect three network protectors to the main switchboard?s main breaker. Space is limited. At the moment, I am showing an ATS and a Distribution Panel on the electrical room wall, and the path of the bus duct goes right over them.
Is this a violation of 110.26(F)(1)(a)? The last sentence of that paragraph says, ?. . . no OTHER (my emphasis) equipment foreign to the electrical installation shall be located in this space.? When you are talking about the Distribution Panel, would the bus duct be considered ?foreign? to its installation? Am I going to have to shuffle some things around?