We replaced 2 A-base meters and 2 old fuse panels in an existing basement with open joist ceiling at 5'11". However, also there were 3 water lines overhead of one of the panels. Our inspector sited 110.26 f-1a and told us one new breaker panel had to move to an adjacent wall. We came back with 110.26 f-1b, which he shot down claiming that only applied to a normal headroom situation (6'6"). My contention then, is if he wants to do that, then we can now use 110.26 E "exception" as this is existing space, build our protection and call it good. Do I have a case?
This was a PM from an electrician from Ithaca, NY. When you have questions, please post your questions for all to address instead of sending a PM to a moderator. Thanks, Charlie