I was wrong, again. I hate it when that happens. In a facility where the sewer pipes must be where they are, my main switchboard grew and placed the corner under it. The height is like 13 feet off the ground, but my gear is 92" plus the pad I think so at least 8 feet off the ground to the top. Nothing at all comes out of the top.
So, my mistake I thought as long as the foreign system was protected and didn't violate the headroom 110.26(E) it could be above the gear. My inspector astutely informed me that the section states the systems are allowed, "above the dedicated equipment space" only. 110.26(F)(1)(b). That just makes zero sense to me.
So it is OK for a structural ceiling to be right above the piece of equipment if over 6 1/2', but a pipe protected by a metal pan can't be 3 or 4 feet above the panel? Yet 6 feet above the panel it is OK. Someone smarter than me, please explain the logic.
So, my mistake I thought as long as the foreign system was protected and didn't violate the headroom 110.26(E) it could be above the gear. My inspector astutely informed me that the section states the systems are allowed, "above the dedicated equipment space" only. 110.26(F)(1)(b). That just makes zero sense to me.
So it is OK for a structural ceiling to be right above the piece of equipment if over 6 1/2', but a pipe protected by a metal pan can't be 3 or 4 feet above the panel? Yet 6 feet above the panel it is OK. Someone smarter than me, please explain the logic.