donselec
Senior Member
- Location
- Aurora, CO, USA
Maybe this has been discussed, I couldn't find it; but I'm trying to differentiate between 110.26(A)(3) which says the height of the workspace must be clear to 6 1/2 feet or the height of the equipment, whichever is greater. Exception 1, in existing dwelling units equipment less than 200 amps is permitted where the space is less than 6 1/2 feet. But then in 110.26(E)(1)(a) Dedicated space must be to a height of 6 feet above the equipment or to the structural ceiling... I have a sub-panel in a residential basement (60 amps) and there are 2 6-inch air ducts supplying fresh air to the furnace room, located on the ceiling above the panel. Which rule is applicable? Perhaps 110.26(E) is for commercial work only (panelboards, switch-gear, etc.? Not sure. Thanks for any help.