I am the engineer on a small retrofit project where some new pool mechanical equipment is being installed into what was existing storage room. The mechanical equipment is pre-fabricated onto a skid, and is essentially a couple pumps with a single point connection at a skid-mounted panel (also prefabricated). The skid is about 6 feet long, half will be located with clearance of ~28" between face of equipment and back wall. Then the wall jogs and the remainder of the equipment has adequate clearance (~8 feet).
I expressed my concern about not meeting NEC working space requirements. The manufacturer got back to me and said they can mount the panel on the left side of the skid (the side with adequate clearance). What concerns should I have about clearances for the rest of the skid? Motor connections, junction boxes, controls, etc.
Thanks!
I expressed my concern about not meeting NEC working space requirements. The manufacturer got back to me and said they can mount the panel on the left side of the skid (the side with adequate clearance). What concerns should I have about clearances for the rest of the skid? Motor connections, junction boxes, controls, etc.
Thanks!