I agree, a foreign system wouldn't be connected with a raceway to the panel above it.Nor do I think I would count the powerwall as "foreign systems" 110.26(E)(1)(b).
You're allowed up to 6" of encroachment so if it's 6" you're good.Assume it is 6” is it a violation? Similar to having a transformer in front of a panel board.
If it's 6" or less it is code compliant. More than 6" then you'll need to get creative, something like this:
View attachment 2559992
I didn't install that but it was done by an electrician on one of our jobs.
I would have never thought of that…
Is that a combination of shallow and deep strut?I didn't install that but it was done by an electrician on one of our jobs.
It's all deep except for the vertical pieces the disco is attached to.Is that a combination of shallow and deep strut?
Yes the vertical portion is 3/4" and the rest is 1½". I know what is depicted gets the job done but IMO it's kind of sloppy.Is that a combination of shallow and deep strut?
That's like asking if something is a combination of black and white and you get the answer "it's all white except the part that is black"!It's all deep except for the vertical pieces the disco is attached to.
I was "specificer" than that.That's like asking if something is a combination of black and white and you get the answer "it's all white except the part that is black"!