Gentlemen; scenario outdoor condensing unit installed less than 36'' from the side of the house to the 220 volt contactor on unit. Unit needs to be serviced and maintained while running. Does 110.26 show this as non code compliant?
 
Gregg Harris said:
Gentlemen; scenario outdoor condensing unit installed less than 36'' from the side of the house to the 220 volt contactor on unit. Unit needs to be serviced and maintained while running. Does 110.26 show this as non code compliant?
IMO yes......

110.26 Spaces About Electrical Equipment.
Sufficient access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.

Equipment. A general term, including material, fittings, devices, ,appliances luminaires, apparatus, machinery, and the like used as a part of, or in connection with, an electrical installation.
 
Thank you gentlemen that was my contension, we are reviewing test questions and others disagreed.
 
cowboyjwc said:
I once told my class, "it's not what you think the answer is that matters, it's what I think the answer is." :D
AHJ is another way to spell God. In my house though the only thing that matters is what the BHJ (blonde having jurisdiction) thinks!:D
 
iaov said:
AHJ is another way to spell God. In my house though the only thing that matters is what the BHJ (blonde having jurisdiction) thinks!:D

Ain't that the truth.:D Actually I was talking about when I give tests. There's always a couple of guys that want to over think it and try to read to much into it. Kinda like here.
 
Last edited:
Status
Not open for further replies.
Top