(3) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 150 mm (6 in.) beyond the front of the electrical equipment.

Are there any exceptions to this code requirement related to the 6" beyond the front of the electrical equipment?
:confused:
 
(3) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 150 mm (6 in.) beyond the front of the electrical equipment.

Are there any exceptions to this code requirement related to the 6" beyond the front of the electrical equipment?
:confused:

What are you hoping to do that you need an exception?
 
110.26a(3)

It came into question while looking at a gas train installation for an air make up unit. The gas train's control panel is located above the valves and set back approximately 24 inches. One must reach over (while standing in front of the panel) the gas train piping in order to press the reset button, or make an adjustment to the temperature controller.
 