Sizing the circuit for an A/C compressor....
According to 440.6(A) we size the wire and breaker per what is on the nameplate. A fairly common compressor will give values of “minimum circuit ampacity” of 30A and a “minimum overcurrent protection” of 50A. Here’s the problem... if you check the spec sheet for a 50A breaker (Siemens QP for example) it shows a wire range of #8-#6 conductors. 110.3(B) says we have to follow all published instructions when installing listed equipment. The breakers are listed to accept a minimum of #8 wire, but the installation allows for a #10 on a 50A breaker. This is done daily and passes inspection. I don’t see a problem as far as a safety or practical installation. I’m looking for clarification as the code is written.
Does landing the #10 violate the listing of the 50A breaker, thus creating a violation per the NEC?
According to 440.6(A) we size the wire and breaker per what is on the nameplate. A fairly common compressor will give values of “minimum circuit ampacity” of 30A and a “minimum overcurrent protection” of 50A. Here’s the problem... if you check the spec sheet for a 50A breaker (Siemens QP for example) it shows a wire range of #8-#6 conductors. 110.3(B) says we have to follow all published instructions when installing listed equipment. The breakers are listed to accept a minimum of #8 wire, but the installation allows for a #10 on a 50A breaker. This is done daily and passes inspection. I don’t see a problem as far as a safety or practical installation. I’m looking for clarification as the code is written.