110.3(B) rules when sizing A/C conductors.

Status
Not open for further replies.
Sizing the circuit for an A/C compressor....
According to 440.6(A) we size the wire and breaker per what is on the nameplate. A fairly common compressor will give values of “minimum circuit ampacity” of 30A and a “minimum overcurrent protection” of 50A. Here’s the problem... if you check the spec sheet for a 50A breaker (Siemens QP for example) it shows a wire range of #8-#6 conductors. 110.3(B) says we have to follow all published instructions when installing listed equipment. The breakers are listed to accept a minimum of #8 wire, but the installation allows for a #10 on a 50A breaker. This is done daily and passes inspection. I don’t see a problem as far as a safety or practical installation. I’m looking for clarification as the code is written.

Does landing the #10 violate the listing of the 50A breaker, thus creating a violation per the NEC?
 
Does landing the #10 violate the listing of the 50A breaker, thus creating a violation per the NEC?

Yes. In that case you would need to use a conductor that was at least as large as the minimum size of the conductor permitted on the terminal of that circuit breaker. You could always run the #10's and splice on a short piece at the CB to be code compliant with the terminal rating.

Welcome to the Forum. :)
 
A fairly common compressor will give values of “minimum circuit ampacity” of 30A and a “minimum overcurrent protection” of 50A.
It should say "maximum overcurrent protection" for the breaker/fuse.

Does landing the #10 violate the listing of the 50A breaker, thus creating a violation per the NEC?
Possibly, but if the terminal properly grips the #10 wire, I don't sweat it.
 
I looked at both Eaton and Siemens CB's in the 2 pole, 50 amp configuration. Siemens lists the conductor range from #8-#4, the Eaton CB lists the conductor range from #14-#1/0.
 
I looked at both Eaton and Siemens CB's in the 2 pole, 50 amp configuration. Siemens lists the conductor range from #8-#4, the Eaton CB lists the conductor range from #14-#1/0.

What did you actually look at for the Eaton? There's no way you can land 1/0 on a 50A BR.
 
Thanks, guys.
Yeah they do say “maximum overcurrent protection”. I just messed that up.
Infinity, that’s what I was thinking, but it never dawned on me to check the wire range of a breaker. As long as it clamped properly, I was good with it. A coworker posed the issue to me the other day and I had to investigate. That’s why I love this field.... never stop learning something new!

thanks
Terry
 
Sizing the circuit for an A/C compressor....
According to 440.6(A) we size the wire and breaker per what is on the nameplate. A fairly common compressor will give values of “minimum circuit ampacity” of 30A and a “minimum overcurrent protection” of 50A. Here’s the problem... if you check the spec sheet for a 50A breaker (Siemens QP for example) it shows a wire range of #8-#6 conductors. 110.3(B) says we have to follow all published instructions when installing listed equipment. The breakers are listed to accept a minimum of #8 wire, but the installation allows for a #10 on a 50A breaker. This is done daily and passes inspection. I don’t see a problem as far as a safety or practical installation. I’m looking for clarification as the code is written.

Does landing the #10 violate the listing of the 50A breaker, thus creating a violation per the NEC?

FWIW, the last few years I have been seeing max OCPD and MCA values that are pretty close to each other. Not sure if this is coincidence or a new "trend", but I think I recall some other people commenting on that too.
 
FWIW, the last few years I have been seeing max OCPD and MCA values that are pretty close to each other. Not sure if this is coincidence or a new "trend", but I think I recall some other people commenting on that too.
I would think that, the closer the numbers, the easier the unit is to start, or has higher running current.
 
I would think that, the closer the numbers, the easier the unit is to start, or has higher running current.
Or has a VFD or other control method that is "soft starting".

Across the line starting units that I have seen recently still have in neighborhood of twice MOCP of what MCA is.
 
I looked at both Eaton and Siemens CB's in the 2 pole, 50 amp configuration. Siemens lists the conductor range from #8-#4, the Eaton CB lists the conductor range from #14-#1/0.
I imagine thats an omission on Siemens part, my guess it the lug on the 40-50A two pole breakers are good down to a #14, As there is almost no difference between the 2 pole 15-30's and the 2 pole 40-50's as to lug size.They probably never considered ART 440 or 430 but I am not Siemens.
It gets interesting if you go to a 60 Amp, Siemens has two different breakers with no distinction on part numbers one goes up to a 3 the other 2/0:
 

Attachments

  • 20180902_140037.jpg
    20180902_140037.jpg
    141.4 KB · Views: 0
I imagine thats an omission on Siemens part, my guess it the lug on the 40-50A two pole breakers are good down to a #14, As there is almost no difference between the 2 pole 15-30's and the 2 pole 40-50's as to lug size.They probably never considered ART 440 or 430 but I am not Siemens.
It gets interesting if you go to a 60 Amp, Siemens has two different breakers with no distinction on part numbers one goes up to a 3 the other 2/0:
Question is are they still producing both or did they make a change and one is older than the other?
 