bphgravity
Senior Member
- Location
- Florida
I have a 208Y/120, 3? service to a restaurant. The engineer performed some calcs as followed:
He shows 26,559 as being the starting SC current with 53.78 A. motor contribution. From this,
F = 1.732 x 93' x 26,559 / 1 x 12,843 x 208 = 1.6014 ,
M = 1 / (1+1.6014) = .3844 ,
26,559 x .3844 = 10,209 A RMS.
1. Where did the 12,843 come from (the "C")
2. If the main breaker is rated at 10,000 and the feeder panel it serves only rated 10,000 AIC with 10,000 AIC rated branch circuit breakers, am I not in compliance with 110.9?
He shows 26,559 as being the starting SC current with 53.78 A. motor contribution. From this,
F = 1.732 x 93' x 26,559 / 1 x 12,843 x 208 = 1.6014 ,
M = 1 / (1+1.6014) = .3844 ,
26,559 x .3844 = 10,209 A RMS.
1. Where did the 12,843 come from (the "C")
2. If the main breaker is rated at 10,000 and the feeder panel it serves only rated 10,000 AIC with 10,000 AIC rated branch circuit breakers, am I not in compliance with 110.9?