- Location
- Billings MT
I have a situation that a 110V power circuit from a power panel fused down to 5A is run to a solenoid valve and some control circuits. They are all run in multiple TC cable in a 2" conduit. This is a class 1 Div 2 area. The control engineer wants to not run ground wires internal to the TC cable as he will have to add terminals to the JB, but instead use the conduit as the ground. I am under the impression that if you are using TC cable, the ground must be integral to the cable. Am I missing something? Is there an exception? Grounds are required in C1D2 areas regardless of voltage.