Davebones
Senior Member
- Location
- North Of Tampa Fl
We had to relocate a 112.5 KVA transformer on the floor that feeds a milling machine . Machine is rated max 270 amps at 208 volts . Realized this transformer has been fed on the primary side with #1 thhn wire fused at 125 amps . The secondary wire is two #1/0 per phase into the machine to the main 300 amp breaker . It looks like the wire was sized one size smaller looking at the machine amperage . This has been like this for probably 20 years with no issues . Is this safe to continue to use this transformer in this configuration ?