Has any one seen this or heard of this.
History: existing AB MCC originally fitted with 1336 drives from Allen Bradley. Retrofitted 3 years ago with PF 755 drives. Same control scheme. 480 to 115V, 200va control transformer. Transformer supplies 115V power for inputs, fans, and contactor. The contactor supplies 480V to the input of the drive. The drive enable and the contactor coil are paralleled. There are two items in the field that can interrupt the contactor and enable, an early break field disconnect and an "enable" from the control cabinet. This makes a possibility of the 115V can be applied to the rest of the 115V input card without the drive being powered up. One month after commissioning 4 separate drives had the drive enable inputs burn up ( meaning 115 was present at the card terminals but the bit was not "high" according to the drive. The 115V input cards were replaced and all was fine, Fast forward 3 years and this time two of the inputs are now scorched ( I can see two scorched components on the card). The card was replaced and it immediately blew the control transformer secondary fuse. To make sure where the control wiring was compromised, I inserted a 100 watt incandescent light bulb in series with the control fuse and by using a clamp on ammeter the "short" was traced to the the 115V input card. None of the field wiring is compromised.
I only bring this up because of another experience with kinetix 6500 drives where the opposite needed to happen ( the drive needed to be powered by 24 volts and "happy" before the 480V was allowed to connected.
I was able to reprogram the drive to be operated by the HIM module for the production gods.
I do have access to the drive while it is running, but I cannot turn it off for another three months. Also during the afore mentioned outage a cleaning crew will have it locked out for most of the day and I will only be able to turn the power on and off for around an hour before the production gods will demand it is running.
History: existing AB MCC originally fitted with 1336 drives from Allen Bradley. Retrofitted 3 years ago with PF 755 drives. Same control scheme. 480 to 115V, 200va control transformer. Transformer supplies 115V power for inputs, fans, and contactor. The contactor supplies 480V to the input of the drive. The drive enable and the contactor coil are paralleled. There are two items in the field that can interrupt the contactor and enable, an early break field disconnect and an "enable" from the control cabinet. This makes a possibility of the 115V can be applied to the rest of the 115V input card without the drive being powered up. One month after commissioning 4 separate drives had the drive enable inputs burn up ( meaning 115 was present at the card terminals but the bit was not "high" according to the drive. The 115V input cards were replaced and all was fine, Fast forward 3 years and this time two of the inputs are now scorched ( I can see two scorched components on the card). The card was replaced and it immediately blew the control transformer secondary fuse. To make sure where the control wiring was compromised, I inserted a 100 watt incandescent light bulb in series with the control fuse and by using a clamp on ammeter the "short" was traced to the the 115V input card. None of the field wiring is compromised.
I only bring this up because of another experience with kinetix 6500 drives where the opposite needed to happen ( the drive needed to be powered by 24 volts and "happy" before the 480V was allowed to connected.
I was able to reprogram the drive to be operated by the HIM module for the production gods.
I do have access to the drive while it is running, but I cannot turn it off for another three months. Also during the afore mentioned outage a cleaning crew will have it locked out for most of the day and I will only be able to turn the power on and off for around an hour before the production gods will demand it is running.