12/2/2 for 2 circuits, sharing the 1 ground

Status
Not open for further replies.

dinotone

Member
Location
Milton
Does it break any code to use 12/2/2 for 2 separate circuits (either 2 120v or 2 240v or 1 of each)? Do they each require their own ground? Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No it's perfectly acceptable. By comparison, you could multiple circuits in a raceway and you're only required to have one EGC.
 

480sparky

Senior Member
Location
Iowegia
You can have as many circuits as you want and they can all share the same ground..... as long as it's sized based on the largest circuit.

You only need separate grounds if it's required by some other reason, such as an isolated ground.
 