12-2 to start 15a circuit

Status
Not open for further replies.

BobbyRay

Member
Where in the code does it allow the home run of a 15a circuit be #12-2 wire, then the rest of the circuit be in #14-2 wire? This is in my opinion a very bad practice. But I've heard that the code allows for this, any thoughts?
 

physis

Senior Member
Re: 12-2 to start 15a circuit

I've never looked up why I'm allowed to use over sized conductors but in general I know you'll find it in Article 310 and I think section 310.15 and subsections should specifically cover it.

[ July 19, 2005, 06:22 PM: Message edited by: physis ]
 

redfish

Senior Member
Re: 12-2 to start 15a circuit

In our area size 14 NM has been banned by the AHJ. I have not ordered 14/2 or 14/3 in years. :)
 

physis

Senior Member
Re: 12-2 to start 15a circuit

Why? Because it's good for 5 amps more than it's usually allowed to be used for. :D

Edit: I primarily use 12 everywhere (residential)and it's a real pleasure when I do use 14 ga. Forcing someone to use larger conductors than necessary is dumb. I'd hate to have to use 10 ga. where I only needed 12 ga. Unless I wanted to. What evil genius came up with this?

[ July 19, 2005, 06:40 PM: Message edited by: physis ]
 

redfish

Senior Member
Re: 12-2 to start 15a circuit

In this case the evil genius is the AHJ, not only in my community , but in the surrounding communities as well. :)
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 12-2 to start 15a circuit

Originally posted by BobbyRay:
Where in the code does it allow the home run of a 15a circuit be #12-2 wire, then the rest of the circuit be in #14-2 wire? This is in my opinion a very bad practice. But I've heard that the code allows for this, any thoughts?
Bob you will not find a spot in the code that 'allows' using larger conductors.

The important thing is that the code does not prohibit using larger conductors.

In larger buildings it becomes necessary to run larger conductors. In my area a common job specification requires 20 amp circuits longer than 100' to be run with 10 AWG.

I have also worked in some very large warehouses that the prints showed 4 AWG for many 20 amp receptacles. In that case they left the panel as 10 AWG to a junction box than switched to 4 AWG and of course the reverse was done at the far end.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 12-2 to start 15a circuit

The reason for this would be more basic electrical theory necessitated (voltage drop as mentioned before) than code driven.

If it makes you feel better, ( to take Iwires example a little farther) you can start with #14 and finish the run with #12 to accommodate the voltage drop, you simply have to calculate what amount of VD you can tolerate on the #14 to a given distance before you calculate the remainder with the #12 to the total you can live with.

Remember the NEC on recommends a maximum voltage drop figure in an FPN, it doesn't mandate a figure.

Roger

[ July 19, 2005, 07:18 PM: Message edited by: roger ]
 

physis

Senior Member
Re: 12-2 to start 15a circuit

I guess you're right Bob, I can't find anything aside from minimums.

Edit: Error B

[ July 19, 2005, 07:19 PM: Message edited by: physis ]
 

rcwilson

Senior Member
Location
Redmond, WA
Re: 12-2 to start 15a circuit

Is someone concerned that a later electrician will see #12 and put it on a 20A breaker?

I agree with not using #14.

When my wife and I built our house(3800 sqft including unfinished basement + 3 car garage), I laid out the 42 circuit panel with 20A CB's for all receptacle and lighting circuits and left 6 spares for future use. I spec'ed all #12. When I was out of the country on a project, the EC pulled all #14 (6100 feet of it)except for the range and used every space in the panel. He claimed that 20 A circuits were a problem with the can lights because putting more than 6 or 8 can lights on a circuit made the cans buzz when the lights were on. So he always used 15A & #14 and ran more circuits. We argued. I didn't pay his full bid price. Was he just trying to make pulling easy or was he right and I was wrong?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: 12-2 to start 15a circuit

Is someone concerned that a later electrician will see #12 and put it on a 20A breaker?
Someone who does this without checking the circuit shouldn't be called an electrician.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 12-2 to start 15a circuit

Originally posted by rcwilson:
Is someone concerned that a later electrician will see #12 and put it on a 20A breaker?
An electrician should know better than to change the OCP for a circuit with out knowing how the circuit is wired.

As for your own house in my opinion you are entitled to specify anything you want and the electrician should follow the specifications that they bid to. :)
 

jbfan74

Senior Member
Location
Newnan Ga
Re: 12-2 to start 15a circuit

The county I live in has not allowed 14 gauge since 94/95. The next county over still allows the use of 14
 

redfish

Senior Member
Re: 12-2 to start 15a circuit

originally posted by rcwilson
He claimed that 20 A circuits were a problem with the can lights because putting 6 or 8 can lights on a circuit made the cans buzz when the lights were on...
To be honest with you, it sounds like someone was pulling your leg, I've never heard of an incandescent recess can buzzing. Maybe your EC had a buzz! ;)
 

mc5w

Senior Member
Re: 12-2 to start 15a circuit

In the house where I lived with my parents back in high school had a 15 amp circuit with a #12 copper home run. Somebody had split the circuit in half and used what they had for the home run. When I got around to changing the electrical service my buddy who was helping me asked why we were using a 15 amp circuit breaker with 20 amp wire.

When I was wiring a factory somebody I know had his kitchen remodeled. He told them to put in 4 circuits for the countertop receptacles rather than 2. Sure enough, these electricians put in 14/3 WG for the home runs and put in 15 amp circuit breakers.

One of the reasons for banning 15 amp wiring is that is the only way that some places can get electricians to put 20 amp wiring into the kitchen, laundry, bathroom, and dining room.
 

allenwayne

Senior Member
Re: 12-2 to start 15a circuit

We had a builder that spec`d 20 amp #12 branch circuits for all lighting and receptacle outlets.
Several years ago I did a house in a high line subdiviion called Cheval,over 12,000 sq ft single story.
The homeowners wanted all the panels 3 of them to be in the garage.The house was shaped like a giant V.Wouldn`t you know it but the kitchen offices(dedicated computer circuits etc.)
were on the opposite end of the house.Some runs were artound 250-275 ft.Break out the 10/2 at panel these circuits were labeled 20 amp only,small piece of sheathing slipped over the conductor and a sharpie marked both sides of the sheathing 20 amp only.
The sad part was when the shop sent another crew to help pull the # 10 h/r`s,one guy asked why all the 240`s.250 ft runs i answered,I was shocked when he said just put fewer light and receptacles on that crcuit :roll: :mad:
 