There would be no way to use it for Article 517 applications. The outer surface is required to be conductive and cannot be covered with PVC.
No, the PVC would cover the conductive surface. The actual outer surface of the wiring method must be suitable for use as an EGC. The outer surface of a PVC coated wiring method is not suitable for use as an EGC.It would still be conductive, no? The pvc would just protect it from moisture. The specific application would be a rewire of dialysis stations.
There would be no way to use it for Article 517 applications. The outer surface is required to be conductive and cannot be covered with PVC.
2005 NEC said:517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas.
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).
(A) Wiring Methods.
All branch circuits serving patient
care areas shall be provided with a ground path for fault
current by installation in a metal raceway system, or a cable
having a metallic armor or sheath assembly. The metal
raceway system, or metallic cable armor, or sheath assembly
shall itself qualify as an equipment grounding return
path in accordance with 250.118.
Is this the section Don?
But wouldn't HCFC cable wrapped in a jacket satisfy that requirement?
2002 NEC said:517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas.
Wiring in patient care areas shall comply with 517.13(A) and (B).
(A) Wiring Methods.
All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable armor or sheath assembly. The metal raceway system, or cable armor, or sheath assembly, shall itself qualify as an equipment grounding return path in accordance with 250.118. Type AC, Type MC, Type MI cables shall have an outer metal armor or sheath that is identified as an acceptable grounding return path.
This link: http://lvhub.wik.is/12-3_MC_Cable
Indicates they have: 12-3 MC AL PVC COATED
....but not an HFC flavor.
yep....it would seem to me that in an HFC flavor, the outer sheathing would still be suitable as an EGC...
Wouldn't the outer sheathing now be PVC and not "an outer metal armor or sheath that is identified as an acceptable grounding return path. "?
It is my understanding that part of the reason for the sheath to be an EGC is to provide the multiple parallel paths that will result when the outer sheath is in contact with other conductive objects. If you coat the outer sheath with PVC you lose these parallel paths.
i don't see how it would be any different than PVC coated rigid....if I take HFC and dip it in PVC, is the outer armor suddenly not the same armor as it was before I dipped it?