mphillipps
Using 12-3, I would like to wire a new kitchen (16 total receptacles) with (2) GFCI breakers. Can this be done? Is there such a thing called "2 pole, 2 throw GFCI breaker"?
Only two circuits for 16 kitchen receptacles?
I agree but it sounds like this is a good size kitchen if there are 16 receptacles. The homeowner is probably expecting more than code minimum.Code only requires two circuits, it does not limit the number of receptacles in residental.
Problem with 2-pole GFCI breaker... one side trips, both circuits are dead.
That's the same thing I was thinking.
Yes it would be to some degree. If you use single pole with handle ties then one could trip without the othe tripping. Also GFCI circuits are more prone to trips then a standard circuit.Would this not be the case with any new, 210.4(B), MWBC? (2008)
I sometimes wrestle with when a 2p should or has to be a "Common" trip. I could see where the wording of 210.4(B) would require the use of a "Common" trip.![]()
I don't think so. I see it as requiring a simultaneous disconnecting not a common trip.Art. 240.15(B) may be a place to read and see that 240.15(B)(1) allows handle ties.
The kitchen is 20 x 12. 17 light fixture and 16 receptacles. Too many light and too many receptacle... but I'm the the architect... just a mere electrician.
It looks like my best option is (2) GFCI receptacles at the start of each run and the other receptacles down stream.
I just want to be sure that I can use 12-3 and use its common neutral and not have the GFCIs trip.