The electrical service from the utility company (Atlantic City Electric) is 12,470/7,200 V 3ph 4wire. We have a 15KV switch gear and then substations transformer to power the building.
I got the minimum 6' required working space from NEC NEC 2020 table 110.34 (A) for the switchgear. But the ACE engineer request at least 8 ft clearance in front of the switchgear. He states that to change the 12kv fuses by a qualified electrician, they would use an 8 ft hot stick so the 6 ft clearance is not enough. Is this true? I mean this is not listed in their handbook or NEC. I would like to here some thoughts from you. Thanks!

I got the minimum 6' required working space from NEC NEC 2020 table 110.34 (A) for the switchgear. But the ACE engineer request at least 8 ft clearance in front of the switchgear. He states that to change the 12kv fuses by a qualified electrician, they would use an 8 ft hot stick so the 6 ft clearance is not enough. Is this true? I mean this is not listed in their handbook or NEC. I would like to here some thoughts from you. Thanks!