12,470 VOLT CABLE EXPOSED IN INDUSTRIAL LOCATION

Status
Not open for further replies.

jbolen

Senior Member
I'm inspecting the electrical on Wate water treatment plant. They have medium voltage cable 12, 470 coming off the end a cable tray about 5 ft off the ground going to a PVC stub up. This building seats 5ft off the ground. The cable is exposed??

Would this possible anywhere in the NEC
 
392.10(B)(2) specifically permits single and multi-conductor cables to be installed in cable tray in industrial occupancies.
However, if the PVC does not stub into the tray, that part of the cable would be a violation, in my opinion.
 
There is no definition of an industrial location. But if the WTP has a 12,470 cable in a tray it would seem to be industrial. Bit the cable needs to be supported like Don said
 