Hello,
I have some portable training electrical equipment that has a 20 amp, 120/ 208V, 3 phase, 5 wire, twist lock plug (L21-20P), on the end. When I first looked at this to size the flexible cord and receptacle that will be hanging down from the strain relief and junction box, I thought-- 20 amps, #12 AWG, with a 20 amp, 3 pole breaker. I purchased some 12/5 SOOW, about 20 feet.
My issue if this:
Table 400.5 (A) (1) for #12 flexible cord Col. A ( 3 conductors ) = 20 amps.
But the plug requires a 5 wire supply as the plug is a L-21-20P. ( 3 ungrounded, 1 neutral grounded, and 1 EGC )
This equipment is 3 phase, using all three ungrounded conductors, so when referring to what the neutral conductor is doing in this circuit I referred to 310.15 (B) (5). Even though I am sure that all 3 loads are NOT balanced, and at some point when this equipment is running there will be some neutral current (incandesent bulbs, signals etc.) can I still treat the neutral as a conductor carrying only unbalanced current, therefore not needing to use the adjustment factors of Table 310.15 (B) (3) (a)- 2011 NEC.
I realize this could all be fine if I just used 10/ 5 SOOW cord, and ran #10 conductors from the panel, but like I said, I already have the cord purchased.
Any thoughts on this?
If I know that this is a 3 phase, 4 wire, wye connected load, am I safe to NOT count the neutral for adjustment even though the loads are NOT balanced. Code article 310.15 (B) (5) says -- carries only unbalanced current, it doesn't say anything about the circuit needing to be balanced in order to not count the neutral as current carrying.
I am starting to confuse myself.
Thanks,
Derrick
I have some portable training electrical equipment that has a 20 amp, 120/ 208V, 3 phase, 5 wire, twist lock plug (L21-20P), on the end. When I first looked at this to size the flexible cord and receptacle that will be hanging down from the strain relief and junction box, I thought-- 20 amps, #12 AWG, with a 20 amp, 3 pole breaker. I purchased some 12/5 SOOW, about 20 feet.
My issue if this:
Table 400.5 (A) (1) for #12 flexible cord Col. A ( 3 conductors ) = 20 amps.
But the plug requires a 5 wire supply as the plug is a L-21-20P. ( 3 ungrounded, 1 neutral grounded, and 1 EGC )
This equipment is 3 phase, using all three ungrounded conductors, so when referring to what the neutral conductor is doing in this circuit I referred to 310.15 (B) (5). Even though I am sure that all 3 loads are NOT balanced, and at some point when this equipment is running there will be some neutral current (incandesent bulbs, signals etc.) can I still treat the neutral as a conductor carrying only unbalanced current, therefore not needing to use the adjustment factors of Table 310.15 (B) (3) (a)- 2011 NEC.
I realize this could all be fine if I just used 10/ 5 SOOW cord, and ran #10 conductors from the panel, but like I said, I already have the cord purchased.
Any thoughts on this?
If I know that this is a 3 phase, 4 wire, wye connected load, am I safe to NOT count the neutral for adjustment even though the loads are NOT balanced. Code article 310.15 (B) (5) says -- carries only unbalanced current, it doesn't say anything about the circuit needing to be balanced in order to not count the neutral as current carrying.
I am starting to confuse myself.
Thanks,
Derrick