- Location
- lawrenceburg kentucky
Hello guys and gals.
"If used on a standard across the line starter, soft start or variable frequency drive, these motors should be wired in the delta (RUN) connection for either high voltage (480V) or low voltage (240V). The only time you should use the wye connection is a wye-delta starter. The final connection of the motor is ultimately the responsibility of the installing electrician. If he has any questions, he should contact his nearest motor specialist prior to energization."
The above paragraph was stated in a manual for a 12 lead dual voltage motor. The motor was first wired up as a wye. The vfd would fault for phase lost. Could you explain to me why wiring the motor as a wye would cause the vfd to trip for phase loss? Just curious.
"If used on a standard across the line starter, soft start or variable frequency drive, these motors should be wired in the delta (RUN) connection for either high voltage (480V) or low voltage (240V). The only time you should use the wye connection is a wye-delta starter. The final connection of the motor is ultimately the responsibility of the installing electrician. If he has any questions, he should contact his nearest motor specialist prior to energization."