NGR circuit on the secondary of a 4.2KV/480V 12 pulse 500kVA transformer. Let through per specification is to be 15A. Load is a 12 pulse AC VFD (VSI)
My experience up to now has been strictly with 12 pulse systems & DC Drives with let through at 1A. All work, but there there are circulating currents between the secondary windings due to a T Resistor circuit for the NGR. An example set up is with 2 x 120 ohm resistors, one connected to the zig zag derived neutral from the DELTA, and the other to the WYE secondary neutral. The ends of these resistors are then tied together and connected to a 277 ohm resistor that is then bonded to the frame ground. Hence the ?T? and the 1A let through in the event of a bolted fault. It is reported to me that if individual NGR circuits from each secondary are directly bonded to frame ground, circulating currents run through the frame and cause problems, problems I do not know the nature of.
I am cautioned that if the T resistor network isn't of a high enough resistance, circulating current can burn up the zig zag on the delta secondary winding.
So - discussion items that have come up in my office:
Deliver a system with 1A let through by interpreting the 15A specified as a maximum only and simply chose a value under this (only because we know the 1A works) but this is a rather large deviation from spec.
Let the delta float and use an NGR on the WYE secondary only. If we bolted one leg of the DELTA to ground, would we expect to see a fault current component flow through the NGR we could use for relaying?
Thanks in advance for anyones thoughts,
My experience up to now has been strictly with 12 pulse systems & DC Drives with let through at 1A. All work, but there there are circulating currents between the secondary windings due to a T Resistor circuit for the NGR. An example set up is with 2 x 120 ohm resistors, one connected to the zig zag derived neutral from the DELTA, and the other to the WYE secondary neutral. The ends of these resistors are then tied together and connected to a 277 ohm resistor that is then bonded to the frame ground. Hence the ?T? and the 1A let through in the event of a bolted fault. It is reported to me that if individual NGR circuits from each secondary are directly bonded to frame ground, circulating currents run through the frame and cause problems, problems I do not know the nature of.
I am cautioned that if the T resistor network isn't of a high enough resistance, circulating current can burn up the zig zag on the delta secondary winding.
So - discussion items that have come up in my office:
Deliver a system with 1A let through by interpreting the 15A specified as a maximum only and simply chose a value under this (only because we know the 1A works) but this is a rather large deviation from spec.
Let the delta float and use an NGR on the WYE secondary only. If we bolted one leg of the DELTA to ground, would we expect to see a fault current component flow through the NGR we could use for relaying?
Thanks in advance for anyones thoughts,