Hi everyone,
On table 310.15(B) (16) THHN on the 75 degree column #12 is rated at 25A**. The ** stands for the maximum overcurrent rating 240.4D which #12 would be 20A. Okay. Table 310.15(B) (3) (a) the adjustment factor of 7-9 current caring conductors is 70% assuming the ambient temperature is 30 Degrees Celsius. In article 100 the neutral is defined as a current caring conductor.
I have a 3/4" EMT conduit with 6 circuits and 2 neutrals and a ground all circuits have a load of 16A. Using the adjustment factor of 70% would I adjust the wire rating using 25A or 20A?
Thank you for your responses.
On table 310.15(B) (16) THHN on the 75 degree column #12 is rated at 25A**. The ** stands for the maximum overcurrent rating 240.4D which #12 would be 20A. Okay. Table 310.15(B) (3) (a) the adjustment factor of 7-9 current caring conductors is 70% assuming the ambient temperature is 30 Degrees Celsius. In article 100 the neutral is defined as a current caring conductor.