Gaffen99
- new jersey
Whats the efficiency difference between a 50 watt low voltage fixture and a 50 watt 120 volt fixture, if there is one ?
well, OK, but theres not voltage number to use on the low voltage size.
Lets assume 18 volts
P = I E
50 = (i) 18
than 50 / 18 = 2.77
For 120 V
50 = (i) 120
than 50 / 120 = .04167
Eff. is output / input : seems like a badly worded question ?
Watts are watts and since there is a pf with the transformer I suspect that the LV is a bit less efficient.
Well I will catch heat for this but 120 volt system is 19,000% more efficient if the load, distance, and wire size are the same.
Lets assume 18 volts.
Besides, the 1:10 ratio of 12v vs 120v makes the math a lot easier.Look at the title 12v vs 120 v
No. Recommend LED's.Sorry, it was 12 volts, A customer keeps asking me to put in low volt lights ( recessed) and I can't convince him that there is not much difference, in the way of going green.
Am I wrong?
Well OK fair enough. Draw yourself a simple circuit diagram of a source voltage, a length or wire, and a load. For example use say 100 feet of 12 AWG. That 12 AWG wire will have resistance with current passing through it which develops voltage drop and power loss. Work it for both voltages and see what you come up with.Now come on, you can't just throw that out without an explanation.
Get your glove ready.Well I will catch heat for this but 120 volt system is 19,000% more efficient if the load, distance, and wire size are the same.
No need for a circuit. The loss difference is a function of the square of the voltages: P = (V^2)/RWell OK fair enough. Draw yourself a simple circuit diagram of a source voltage, a length or wire, and a load. For example use say 100 feet of 12 AWG. That 12 AWG wire will have resistance with current passing through it which develops voltage drop and power loss. Work it for both voltages and see what you come up with.
Don't see the 19,000%, more like 100x
And using the circuit:
100 ft, 50W, #12AWG, 104 deg F
120 volt: 0.148 volt drop, 0.17739 ohms => 0.12319 W
12 volt: 1.48 volt drop, 0.17739 ohms => 12.319 W
add: you said efficiency so:
50.123 W vs 62.319 W for 50 W
99.75% vs 80.23% = 19.52% more efficient
Because that seemed to be the essence of post #16. I found nothing interesting to add concerning the rest of the thread that had not already been said.But your formula is comparing both voltages at 100'. It's likely that the 12v integral transformer will only be a few inches from the lamp. I don't seen any reference to remote transformers in the OP.
As for anything else:
Winnie pretty much covered most it in #5 when he essentially said there are too many variables.
You can find LV lighting can and lamp combos that are more efficient but on the other side of the coin, why not just use a regular can and install a bulb that is more energy efficient than the incandescent?
As for lumen output, I think I read that incandescents are about 15% efficient (a lot of heat, very little light) but LEDs can be something like 85%. I think the CFLs put out something like 4-5 times the lumens per watt of an incandescent (8-10 times for LEDs).
As the OP said in #7, it can pretty much be a wash but, in my opinion, if the customer wants LV, give 'em LV.