Hi i am understanding a 120/208 3 Phase service needs to have 3 conductors, one for each phase brought from the utility secondary. This service is a Wye formation, so we need to bring the neutral from the utility transformer wye secondary as well. My question is do I need to bond my neutral and ground at the service panel if I am bringing a neutral from the utility? I am currently showing a 120/208 3 phase service that bonds the neutral and grounding electrode conductor at the panel. I thought I could "derive" my own neutral at the panel and not pull a neutral from the utility. Would this be a 3 wire panel then?
Can I show a 3 wire panel and derive my own neutral at the panel and not pull a neutral from the utility? ( I have single phase 120V loads)
Should I show a 4 wire panel and pull a neutral from the utility? Do I need to show a bonding jumper at my panel in this case?
Thank you, just trying to get this confirmed.