Does the nuetral conductor for a set of feeders on a 120/208V 3 phase Wye service originating from the MSB running to a panelboard count as a CCC?

I think not because it would be carrying only the unbalanced current according to 310.15(B)(5)(a).

Thanks!

Sent from my SM-N960U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Only if the load is more than 50% harmonic. Not very likely so the answer is no but for the heck of it what is the type of loads being served?
 

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Okay thats what I thought.

Its at a school, mini split hvac units, plugs, lights, etc. Not much in harmonic loads that I would think- except do mini splits have harmonic distortion with their electronics?

Sent from my SM-N960U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Okay thats what I thought.

Its at a school, mini split hvac units, plugs, lights, etc. Not much in harmonic loads that I would think- except do mini splits have harmonic distortion with their electronics?
Given the nature of the building and its loads the neutral is not considered a CCC for derating purposes.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
One caution: if you are running so called 'single phase' feeders from a wye source, then the neutral _is_ a CCC.

You need all 3 hots and the neutral for the neutral to be balanced.

Jon
 

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Yes thanks Jon. I remember seeing that on a Mike Holt and Ryan Jackson video.

Sent from my SM-N960U using Tapatalk
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Only if the load is more than 50% harmonic. Not very likely so the answer is no but for the heck of it what is the type of loads being served?
Really depends on the facility. Think about it, all LED drivers, lighting ballasts, every electronic device. With the exception of resistive heating and motors, it's all electronic now.

Sent from my BE2028 using Tapatalk
 
Really depends on the facility. Think about it, all LED drivers, lighting ballasts, every electronic device. With the exception of resistive heating and motors, it's all electronic now.

Sent from my BE2028 using Tapatalk
But just because something is "electronic" that doesnt mean it will be highly harmonic or non linear. Pretty much everything now has PF correction and generally pretty "clean" power supplies. Its just really not an issue 99% of the time.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Really depends on the facility. Think about it, all LED drivers, lighting ballasts, every electronic device. With the exception of resistive heating and motors, it's all electronic now.
Still wouldn't matter in a new modern building. It would be extremely unlikely in a school to get above 50% harmonic loads on a panel. With modern equipment we're almost at the point where we can forget about high harmonic loads completely.
 