120/208 panel and dead SPARE breakers

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I apologize if this is a stupid question. I do not have much experience with commercial work.

I was called to a small office building. For two years the lights in one of the offices have not worked. I found the correct breaker and determined there was no current from the breaker. I switched the wire to a nearby SPARE breaker and there still was no power. I then realized there was no power in every third SPARE breaker.
I double tapped to an adjacent breaker and all is good.

The panel was labeled 120/208 volts.
There were five conductors connected to the panel (L, L, L, N, G). I did not confirm that the third leg had power.

What is up with every third SPARE breaker with no power?
 
Get in the habit of taking all possible voltage measurements, not just the easy to make Line to Ground ones.
L1-L2
L2-L3
L3-L1
L1-N
L2-N
L3-N
L1-G
L2-G
L3-G
N-G
 
It could be fed from a Delta high leg and they skipped the high leg to avoid having 208V to ground/neutral. If it had L-L-L-N present, I bet the high leg was not connected at that panel or from where it was fed from.
 
It could be fed from a Delta high leg and they skipped the high leg to avoid having 208V to ground/neutral. If it had L-L-L-N present, I bet the high leg was not connected at that panel or from where it was fed from.
That would the panel in question samewhat safer.
 