Greg1707
Senior Member
- Location
- Alexandria, VA
- Occupation
- Business owner Electrical contractor
I apologize if this is a stupid question. I do not have much experience with commercial work.
I was called to a small office building. For two years the lights in one of the offices have not worked. I found the correct breaker and determined there was no current from the breaker. I switched the wire to a nearby SPARE breaker and there still was no power. I then realized there was no power in every third SPARE breaker.
I double tapped to an adjacent breaker and all is good.
The panel was labeled 120/208 volts.
There were five conductors connected to the panel (L, L, L, N, G). I did not confirm that the third leg had power.
What is up with every third SPARE breaker with no power?
I was called to a small office building. For two years the lights in one of the offices have not worked. I found the correct breaker and determined there was no current from the breaker. I switched the wire to a nearby SPARE breaker and there still was no power. I then realized there was no power in every third SPARE breaker.
I double tapped to an adjacent breaker and all is good.
The panel was labeled 120/208 volts.
There were five conductors connected to the panel (L, L, L, N, G). I did not confirm that the third leg had power.
What is up with every third SPARE breaker with no power?