chrisjhn41
New member
Say you have a 30 ckt 120/208 panel, with the A,B,C phase KVA each totaling 14KVA, would that make the total KVA for the panel 42KVA (14KVA x 3phase) and the panel need to be sized at 150A, or would the total KVA be around 25KVA ((14KVAx3phases)/sqrt of 3) and then the panel would be sized at 100A.
In relation to that question, if the above mentioned panel is a sub panel from a 400A 120/208 panel what size does the CB in the 400A panel feeding the above panel need to be?
It seems to me that if each phase is carying a 14KVA load that the panel and breaker would need to be sized for at least 150A and each phase feed wire would also need to be sized that way, but i have been told to size the breaker and feeders for the 25KVA calculated as shown above and feed size by the 25KVA @ 208 3phase for 100A.
Can anyone shed some light on this situation so i have a better understanding as to how the KVA per phase related to the total panel KVA?
In relation to that question, if the above mentioned panel is a sub panel from a 400A 120/208 panel what size does the CB in the 400A panel feeding the above panel need to be?
It seems to me that if each phase is carying a 14KVA load that the panel and breaker would need to be sized for at least 150A and each phase feed wire would also need to be sized that way, but i have been told to size the breaker and feeders for the 25KVA calculated as shown above and feed size by the 25KVA @ 208 3phase for 100A.
Can anyone shed some light on this situation so i have a better understanding as to how the KVA per phase related to the total panel KVA?