hoots
Member
- Location
- Gary, Indiana, U.S.A.
My brother-in-law is needing to string up a 3phase, 150amp, 120/208 service 750' away for his irrigation pump and lighting/120 power. After looking at table 310.68 in the nec 2008 code, it's saying that 1/0 aluminum (triplexed in air) is good for 170 amps. Now after doing a quick calculation of voltage drop, i came up with around 30 volts dropped at that length. just wondering if this sounds right, and if it would be more efficient to either stay with the 1/0 that's rated for the ampacity needed, and get a transformer to boost the voltage up another 30 volts. or to go with lets say 4/0 that would greatly reduce the amount of v.d. I'm worried about weight and span with the 4/0 in the air...Thanks!