Can 3- 4" conduits with 4 -500mcm cu. conductors be paralled. It's a long story!
I couldn't tell you about the 6" weatherhead but damn it'll be big......
It's my understanding that since you're feeding more than one service disconnect, your service conductors are sized to the load rather than the combined OCPD of your service disconnects. 230.42(A)
I always have had a problem with the way 230.42(A) especially (A)(1) is worded. It states "The sum of the noncontinuous loads plus 125 percent of continuous loads." It DOES NOT state something to the effect of "shall have an ampacity not less than the calculated load to be carried, determined in accordance with Part III, IV, or V of Article 220, as applicable", similar to the wording in 230.79. As it is currently worded, to me that's saying one cannot apply any demand factor to the load when sizing the service entrance conductors...I agree with Cow on both counts.
Indeed it is. A 2014 proposal in the making...Samrt$, Very interesting comments..cause for thought.
Oh, I know. I was just pointing out the general section comparable to 240.4(B) that Chris commented on, but only applies to feeders, and had since been clarified that we are discussing service conductors... but I suppose I should have elaborated...Note, however, in regard to 230.90, there are exceptions to the basic statement you quoted which allow for calculated load.