kda3310

Senior Member
I have to install a sub panel 120/240 single phase on to a 120/208 three phase system as per instructions of my boss. What I would like to know is there a problem with running 240 equipment on a 208 system and why do we have these two nominal voltage systems.

Sent from my XT1565 using Tapatalk
 

peter d

Senior Member
Location
New England
I have to install a sub panel 120/240 single phase on to a 120/208 three phase system as per instructions of my boss. What I would like to know is there a problem with running 240 equipment on a 208 system

It will be a problem if any of the equipment is not listed for use on 208 volt systems.

and why do we have these two nominal voltage systems.

120/240 is single phase and 120/208 is 3 phase. They co-exist because single phase is most practical for residential and most small/medium commercial while 3-phase is better for anything beyond that.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I have to install a sub panel 120/240 single phase on to a 120/208 three phase system as per instructions of my boss. What I would like to know is there a problem with running 240 equipment on a 208 system and why do we have these two nominal voltage systems.

Sent from my XT1565 using Tapatalk

Wait, do you have both voltages there now?
If not and it's only a 208/120, you can't get 240V out of that.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
But you can use a panel rated for 120/240 for a two out of three phase application. Just be careful with MWBCs.

Yes, but my reply was in thinking the OP was needing to have actual 240/120 voltages.
I might have read him wrong as he could be asking about the panel rating only.
 

MNSparky

Senior Member
Location
Minneapolis, MN
Occupation
Electrical Contractor - 2023 NEC
Yes, but my reply was in thinking the OP was needing to have actual 240/120 voltages.
I might have read him wrong as he could be asking about the panel rating only.

I read it like that, too.

You have to be careful that the 240v equipment is also rated for 208v. There may be taps to change internally especially if it has low voltage controls, like HVAC equipment.

There's a condo complex that uses us for the maintenance and we get regular calls from condo owners that just replaced their range. They buy a standard 240v residential range and then are confused why it takes an hour for it to get up to temp. I usually explain the issue to them and tell them to call the appliance people back out. I've heard there are taps you can change in the ranges but I've never dug into myself.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I read it like that, too.

You have to be careful that the 240v equipment is also rated for 208v. There may be taps to change internally especially if it has low voltage controls, like HVAC equipment.

There's a condo complex that uses us for the maintenance and we get regular calls from condo owners that just replaced their range. They buy a standard 240v residential range and then are confused why it takes an hour for it to get up to temp. I usually explain the issue to them and tell them to call the appliance people back out. I've heard there are taps you can change in the ranges but I've never dug into myself.

Some may have taps, but the ones I am familiar with require changing elements.
For water heaters you can get either single voltage elements or dual voltage 208/240 with a tap.
 

kda3310

Senior Member
Yes, but my reply was in thinking the OP was needing to have actual 240/120 voltages.
I might have read him wrong as he could be asking about the panel rating only.
This is our plant administration offices. It is all 3 phase 208. They want to hook up a mobile hearing test booth to it that has been running on a 1 phase 120/240 generator. I don't know what the both requires. I'm only doing what my boss is telling to do. I'm hoping there is not going to be any problems.

Sent from my XT1565 using Tapatalk
 

Electric-Light

Senior Member
This is our plant administration offices. It is all 3 phase 208. They want to hook up a mobile hearing test booth to it that has been running on a 1 phase 120/240 generator. I don't know what the both requires. I'm only doing what my boss is telling to do. I'm hoping there is not going to be any problems.

Sent from my XT1565 using Tapatalk

What's a mobile hearing test booth? Is that like a trailer with hearing test stuff and things like AC and interior lights? I would guess the test equipment and lights runs on 120v meaning that it wouldn't matter at all. The wall pack AC is probably 208-230
 

JFletcher

Senior Member
Location
Williamsburg, VA
I have to install a sub panel 120/240 single phase on to a 120/208 three phase system as per instructions of my boss. What I would like to know is there a problem with running 240 equipment on a 208 system and why do we have these two nominal voltage systems.

Sent from my XT1565 using Tapatalk

Some 240V rated equipment will not be happy on 208V. A hearing test trailer should have 120V equipment for the testing, so whether it's fed from a 120/208 or 120/240V source *shouldnt* matter.

As to your second question, residential service is often single phase (split phase or center tap neutral), with 120V to neutral but 240V line to line. Commercial transformers are often 3 phase and due to phase angle, 120V to neutral gives 208V line to line. There are open delta transformer banks that have 240V line to line, but the B phase is 208V to neutral. Why have 120, 208, 240, 277, 480V here? Different demands of equipment is one answer. A 900HP aeration blower would be wired to 4160V, you could wire it 480V or even 120V if you could make conductors that would carry 4,000+A. Cheaper to make better insulation and smaller wire.
 

Mike Furlan

Member
Location
Lemont Il
Some 240V rated equipment will not be happy on 208V. A hearing test trailer should have 120V equipment for the testing, so whether it's fed from a 120/208 or 120/240V source *shouldnt* matter.

As to your second question, residential service is often single phase (split phase or center tap neutral), with 120V to neutral but 240V line to line. Commercial transformers are often 3 phase and due to phase angle, 120V to neutral gives 208V line to line. There are open delta transformer banks that have 240V line to line, but the B phase is 208V to neutral. Why have 120, 208, 240, 277, 480V here? Different demands of equipment is one answer. A 900HP aeration blower would be wired to 4160V, you could wire it 480V or even 120V if you could make conductors that would carry 4,000+A. Cheaper to make better insulation and smaller wire.

Just don't change the taps on the transformers, as I've seen done to get 240V on a three phase transformer (wanted the hot water heaters to heat faster). They had 130V to neutral, and didn't notice it for years.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I have to install a sub panel 120/240 single phase on to a 120/208 three phase system as per instructions of my boss. What I would like to know is there a problem with running 240 equipment on a 208 system and why do we have these two nominal voltage systems.

Sent from my XT1565 using Tapatalk

This is a pretty common practice in apartment buildings where all the loads in the unit are 120V.
 

kentirwin

Senior Member
Location
Norfolk, VA
This is our plant administration offices. It is all 3 phase 208. They want to hook up a mobile hearing test booth to it that has been running on a 1 phase 120/240 generator. I don't know what the both requires. I'm only doing what my boss is telling to do. I'm hoping there is not going to be any problems.

Sent from my XT1565 using Tapatalk

Every mobile hearing test provider I've had experience with wants 2 dedicated 120V circuits.
 

Electric-Light

Senior Member
Just don't change the taps on the transformers, as I've seen done to get 240V on a three phase transformer (wanted the hot water heaters to heat faster). They had 130V to neutral, and didn't notice it for years.

Every mobile hearing test provider I've had experience with wants 2 dedicated 120V circuits.

Which makes sense. Some loads have a very abrupt load changes and cause a dip. You usually want equipment sensitive to sag and notching separate from house load to keep them away from notches and spikes.
 