Hi Guys,
I design one project that we use 120/208V 3 phase service. But our client prefer to use one 380V 12kW equipment.
Could we use this panel to feed this 380V equipment?
If so, what is the breaker size for this equipment?
12000*1.25/(1.732*208)=41.6Amps. Should I use 50 Amps breaker for this equipment?
I really appreciate any suggestion.
Best,
David