Hello all,
I'm working on a job that has a new 120/208V 4-wire wye service. From that new new service (which is a 1000A fused switch), it feeds a 300 Kva transformer. The transformer is a 120/208V wye primary, and 480V delta secondary. From the 300 Kva transformer, it feeds a 480V panelboard, with a main breaker.
My question is this: How would I properly bond the transformer? At the service disconnect, the nuetral and ground are bonded. Normally, I wouldn't bond the XO terminal at the transformer, since it's bonded at the service. The 480V delta panel has no neutral, so would I simply land the EGC at the transformer case? I landed the GEC at the 480V panel, and of course there is a separate GEC at the 208V main service.
Thanks in advance!!
Andy
I'm working on a job that has a new 120/208V 4-wire wye service. From that new new service (which is a 1000A fused switch), it feeds a 300 Kva transformer. The transformer is a 120/208V wye primary, and 480V delta secondary. From the 300 Kva transformer, it feeds a 480V panelboard, with a main breaker.
My question is this: How would I properly bond the transformer? At the service disconnect, the nuetral and ground are bonded. Normally, I wouldn't bond the XO terminal at the transformer, since it's bonded at the service. The 480V delta panel has no neutral, so would I simply land the EGC at the transformer case? I landed the GEC at the 480V panel, and of course there is a separate GEC at the 208V main service.
Thanks in advance!!
Andy