Is a 120/208Y distribution system cheaper when 480-120/208 step down transformer losses are taken into account?
Cheaper than what?Is a 120/208Y distribution system cheaper when 480-120/208 step down transformer losses are taken into account?
Cheaper than what?
Do you mean is a 208Y/120 system less expensive than a 480Y/277 volts system that utilizes transformers to create the 208Y/120 volt?
You should start with the total calculated load.
How much of that is/could be 480/277?
I think you're going to have to provide a lot more information on the givens and assumptions we are to make. I'm reading this like you're asking if owning a car is cheaper than uber if you factor in leaving a tip.
I'd be shocked if a building that needs 2 MW of service only has 120 or 208V loads.
I think part of the equation is that HVAC can be 480V, lighting can be 277V, etc.
Jon
Basically a 2,500 or 3000 amps 480 volt service vs a 5000 or 6000 amp 120/208Y service.
I'm wondering if the saving in wire will offset all the idiling losses.
Right, but you can get units at 120/208, especially if packaged or roof top.
I wasn't thining about service size, I'm asking about the loads- are all the loads 208/120 or can/are some of them 480? And are those less expensive than 208v equipment?Basically a 2,500 or 3000 amps 480 volt service vs a 5000 or 6000 amp 120/208Y service.
I wasn't thining about service size, I'm asking about the loads- are all the loads 208/120 or can/are some of them 480? And are those less expensive than 208v equipment?
IMO the 480Y/277 would be better for this. Someone once told me the crossover point was about 500kva of load where the 480 service would become more economical, that was many years ago so I'm unsure if that number still is good.5000 amp vs 2500 amp calculated service.