The question I have is to whether or not the location that I am inspecting has adequate power. The facility is a single story, multi-room berthing (it is on a military installation in So Cal), somewhat like a motel. My command has been tasked with renovating two of the rooms. Upon inspection, the building is supplied by 120/208Y instead of single phase 120/240 (not sure why since there are no 3-phase loads). The rooms that we are renovating require a new sub panel which is how this issue arose. My question is, looking at ANSI C84.1, if you follow the 95% to 105% rule, this will not be acceptable for the 240V dryer and range being installed. If you follow the 87% to 106% it is okay. I think they NEED to install a new poletop transformer to provide this building with 120/240, but not sure if the HAVE to. Any help would be greatly appreciated.