Re: 120/240 GFCI Requirement
My objective is to use two-gang wall boxes with each furnished with a 120V duplex and a 240V duplex receptacle. This is a one-man shop, so one circuit is sufficient as only one machine is in use at a time. I have pulled a single 3-conductor cable through my finished shop walls, and everything works fine. In fact, I also control my central dust collection system by sensing machine current (red conductor) at the breaker and using that to switch power to the dust collector motor. So when a machine is turned on and off, the dust collector comes on and off automatically. The 120V receptacles are fed from the black wire, so their current doesn't control the dust collector. Actually, I do feed the 120V chop saw and router table from the red so they do control the dust collector, too.
The advantage is you only have to pull one cable, and the boxes are less cluttered with only four conductors entering and leaving rather than the six you would have with a pair of 2-conductor cables, one for 120V and one for 240V. I am planning to write this up for publication, so I need to cover the GFCI requirement.
The 120V GFCI requirement can be satisfied by using a 120V GFCI outlet at each receptacle location; the usual "downstream" connection will not work since it depends on a current balance in the hot and neutral conductors to the downstream receptacles. When a 240V machine is turned on, the 120V GFCI will trip because of the current imbalance in the downstream hot and neutral conductors. But using a GFCI for each 120V receptacle will work.
Similarly, using a 240V GFCI breaker will not work either since when a 120V load is applied, the current will not balance in the two hot conductors, tripping the breaker.
My basement shop is old work (previously a finished room with a rug) with finished walls but an epoxy painted cement floor. If it were new work, I would use separate conductors for 120V and 240V, each protected with a GFCI breaker, but I'd probably need to use separate boxes for 120V and 240V with the extra wire as mentioned above.
The question really is, does the code require GFCI protection for 240V receptacles? If not, then this system, while not a standard wiring plan, appears to meet the code. If 240V receptacles require GFCI protection, then it will not meet code. A publisher will certainly ask that question.
Bruce